ControlLogix, GSV of WallClockTime into a UDT, DST happened, batch records shifted. NTP is 'someone else's job.' Do you freeze PLC time to UTC and convert in the historian, or keep local and eat the DST fight?
On-site nationwide · Legacy and current platforms
On-site nationwide
Allen-Bradley
Nadia Petrov · Batch
ControlLogix, GSV of WallClockTime into a UDT, DST happened, batch records shifted. NTP is 'someone else's job.' Do you freeze PLC time to UTC and convert in the historian, or keep local and eat the DST fight?
Anika Bose · OT architect
UTC in the processor. Convert at the historian and the HMI. DST in a PLC is how you get a two-hour hole or a duplicate batch ID. Pin NTP to a plant source, not a laptop. If you must stay local, disable DST on the controller and document it in the SOP so the next guy doesn't 'fix' it.